Posted: Fri Jul 06, 2012 1:33 am Post subject: current leakage on my solenoid valve coil |
|
|
can any one help me to understand the reason behind the leakage of current from my solenoid coil.
this was not the case earlier when I checked |
|
|
| Back to top |
|
 |
Trayderji Frequent Visitor to IAH

Joined: Jun 16, 2011 Posts: 108 Location: Navi Mumbai
Status: Offline
|
Posted: Fri Jul 06, 2012 8:31 am Post subject: Re: current leakage on my solenoid valve coil |
|
|
Emmanuel:
Current leakage can due to be moisture, specially during monsoon, check whether it is leakage current or there is a short in the selenoid coil,
if it is leakage current then dry the coil completed either in the sun or by an hot hair dryer, if it is short then it need to be replaced. |
|
|
| Back to top |
|
 |
josyjames Committed Member of IAH

Joined: Apr 21, 2010 Posts: 1882 Location: Bangalore-Ramamurthy Nagar
Status: Offline
|
Posted: Fri Jul 06, 2012 9:32 am Post subject: Re: current leakage on my solenoid valve coil |
|
|
| Are you using a Three PIN socket? (I mean which has Earth point connected) |
|
|
| Back to top |
|
 |
aquariumer Regular Poster on IAH

Joined: Sep 06, 2010 Posts: 1097 Location: Mumbai-Thane
Status: Offline
|
Posted: Fri Jul 06, 2012 11:34 am Post subject: Re: current leakage on my solenoid valve coil |
|
|
| Trayderji wrote (View Post):
|
Emmanuel:
Current leakage can due to be moisture, specially during monsoon, check whether it is leakage current or there is a short in the selenoid coil,
if it is leakage current then dry the coil completed either in the sun or by an hot hair dryer, if it is short then it need to be replaced.
|
yes I had done soap test may be due to it
@Shelly no Iam not using earthing line |
|
|
| Back to top |
|
 |
josyjames Committed Member of IAH

Joined: Apr 21, 2010 Posts: 1882 Location: Bangalore-Ramamurthy Nagar
Status: Offline
|
Posted: Fri Jul 06, 2012 12:31 pm Post subject: Re: current leakage on my solenoid valve coil |
|
|
| You need to use earthing for the solenoid. Once you open the solenoid, you can see three terminals. |
|
|
| Back to top |
|
 |
aquariumer Regular Poster on IAH

Joined: Sep 06, 2010 Posts: 1097 Location: Mumbai-Thane
Status: Offline
|
Posted: Fri Jul 06, 2012 1:59 pm Post subject: Re: current leakage on my solenoid valve coil |
|
|
| yes there is earthing point but I never been using that line in my other coils and I had never had currents leakages even after soap tests |
|
|
| Back to top |
|
 |
Trayderji Frequent Visitor to IAH

Joined: Jun 16, 2011 Posts: 108 Location: Navi Mumbai
Status: Offline
|
Posted: Thu Jul 12, 2012 7:41 pm Post subject: Re: current leakage on my solenoid valve coil |
|
|
| aquariumer wrote (View Post):
|
|
yes there is earthing point but I never been using that line in my other coils and I had never had currents leakages even after soap tests
|
Was your problem solved?  |
|
|